what table list these cubic in?

Status
Not open for further replies.

steveng

Senior Member
Location
Texas
?Determine the minimum cubic inches required for two 10 TW conductors passing through a box, four 14 THHN conductors spliced in the box, two 12 TW conductors terminating to a receptacle, and one 12 AWG equipment bonding jumper from the receptacle to the box.
 

480sparky

Senior Member
Location
Iowegia
Start at 314.16(B). 10s require 2.5 in? (1), 14s require 2 in? (1), 12s require 2.25 in? (1), device is counted as 2 12s (4), ground wire counts one 12 (5). I'm not sure about the 14s. Are there two coming in and two going out, or four coming in and four going out? TW and THHN are simply to throw you off. In box fill, 10s are 10, regardless of insulation.
 
Last edited:

steveng

Senior Member
Location
Texas
:grin: i see it now, thanks
i had a brain fog...
i could'nt see the forest for the trees

thats 22.5, cu in. , right?
 
Last edited:

480sparky

Senior Member
Location
Iowegia
I get 24.25

Two 10s @ 2.50 = 5.00 (1)
four 14s @ 2.00 = 8.00 (1)
Two 12s @ 2.25 = 4.50 (1)
Two more 12s for the device @ 2.25 = 4.50 (4)
One #12 ground @ 2.25 = 2.25 (5)
 

steveng

Senior Member
Location
Texas
the answer in the test was 22, ( mikes, test)
i did not count the bonding jumperd egc, since it does not leave the box.
314.16 B 1
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
steveng said:
the answer in the test was 22, ( mikes, test)
i did not count the bonding jumperd egc, since it does not leave the box.
314.16 B 1

I agree with you that the bonding jumper does not get counted. I bet sparky knows that but was thinking there was an EGC in the box. Answer is 22 cu. inches
 