robert pitre Member Location Houma,la Oct 15, 2015 #1 What table in the NEC 2011 that we use for sizing grounds?
F Fitzdrew516 Senior Member Location Cincinnati, OH Oct 15, 2015 #2 Depends what "ground" you're talking about.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Oct 15, 2015 #3 250.122 for the equipment grounding conductor 250.66 for the grounding electrode conductor 250.102(C)(1) for bonding jumpers
250.122 for the equipment grounding conductor 250.66 for the grounding electrode conductor 250.102(C)(1) for bonding jumpers
robert pitre Member Location Houma,la Oct 15, 2015 #4 Dennis Alwon said: 250.122 for the equipment grounding conductor 250.66 for the grounding electrode conductor 250.102(C)(1) for bonding jumpers Click to expand... Thanks Dennis