Timer being feed by 14-3. Two loads going out. Customer doesn't want the timer anymore. He wants both loads to be on a photocell instead. Federal pacific panel FYI. One of the loads I have to protect with a GFCI. So it sounds like I'll need two photocells. Or do they make one that will turn on two loads? Will a GFCI work in this application? Or will it sense a imbalance. Both of these loads are lighting, if that matters. One is exterior, and one is landscape. Thank you for your help.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Possibilities:

1. Photocell controls a 2-pole relay.

2. Both loads on a single circuit if possible.

3. Two photocells.

If the GFCI device is a receptacle, you should be okay.
 