Hello, a theoretical question here...grounding related - at a transformer: primary= single phase 480 (two ungrounded conductors and one equipment grounding conductor) ... secondary= single phase 240 with a grounded neutral. This transformer has a system bonding jumper within: GEC, equipment bonding jumper (to transformer metal + first disconnect), and neutral from transformer = all bonded within the transformer.
If one of the secondary legs has a ground fault within the transformer, what is the electrical path which causes the primary breaker to trip? There is a low impedance ground path back to the primary panel.... The primary conductors energize one side of the transformer, which is isolated from the metal shell/frame of the transformer. However, if one leg on the secondary ground faults to the metal shell/frame of the transformer, I can't see the path which causes the primary to trip....Thanks, Gus Long
If one of the secondary legs has a ground fault within the transformer, what is the electrical path which causes the primary breaker to trip? There is a low impedance ground path back to the primary panel.... The primary conductors energize one side of the transformer, which is isolated from the metal shell/frame of the transformer. However, if one leg on the secondary ground faults to the metal shell/frame of the transformer, I can't see the path which causes the primary to trip....Thanks, Gus Long