Should I use the voltage rating of the motor (230V) to select the drive or the POCO voltage of 208Y? The drive is the variable in this equation.
Should I use the voltage rating of the motor (230V) to select the drive or the POCO voltage of 208Y?
I agree with what you have said. If the Pton wants to get full rating from his motor, a drive with a boost converter would be one way to go. Maybe a step up autotransformer on the input would be cheaper?Most drives will only be able to produce an output voltage equal to the input voltage. If you reduce the maximum speed of the motor then the drive will be able to support proper magnetization. Some drives have a boost converter on the input stage; these can produce higher output voltage than input. Examples are drives capable of line regeneration.
-Jon
Never thought about a buck/boost transformer on the incoming. Good idea for future, Could I elimnate a line side reactor by using buck/boost(s)?
I don't know if you can use a buck-boost in this fashion. When I last installed a line regen drive, the documentation specified a certain required impedance on the supply side, which could be provided by a line reactor _or_ transformer.
-Jon
I would think you should specify both, the supply and the load, since both are variables when selecting VFD's.Should I use the voltage rating of the motor (230V) to select the drive or the POCO voltage of 208Y?