Since the refrigerator is a relatively constant load, I would suggest a buck boost transformer at the far end to correct the voltage. And if you have two refrigerators, then I would consider putting in a small panel with #4 conductors.
Buck boost transformers are not a good idea for correcting voltage drop. If you have desired voltage when circuit is loaded, you will have too high of voltage when there is little to no load. Running larger conductor often cost less anyway. Had the OP been running say 1500 feet, then maybe you are getting close to enough length the cost difference may be significant enough, but use step up then step down on each end not a buck/boost.
The refrigerator will be on its own circuit.
FL A is 6A. Thanks for clearing it up that NEC recommends no more than 3% I was thinking it was 5%. So with 4ga wire and an fla rating at 6A. This should be fine on a 20a circuit?
Voltage drop will be significantly less for 6A then the 16A most have been talking about.
But since you have two refrigerators you do have 12A if on one circuit. You still will have extra drop when compressor(s) is starting.
Multiwire circuit may be helpful here - if only one refrigerator is running - you have voltage drop for 6A @ 120 volts. If both are running you have voltage drop for 6 A @ 208 or 240 volts. (208 is a little more complex because of the 120 deg phase angle, but if you size conductors for the 6A @ 120V you will be fine.