Have to set a new underground fed 100 amp rated 240 volt sub panel 170' away from main service. Total load at sub panel will be a (used once in a while) 50 amp RV receptacle, a 4 amp load for a small 120 volt "bunny den" AC unit, a small 4 amp under counter refrigerator for a BBQ Island and then several convenience receptacles for the BBQ Island and a ceiling fan for a new pagoda. I figure a #4 CU 70 amp feeder in an 1-1/4" PVC conduit will still be fine, but am a bit concerned about voltage drop. Don't want to have to pull #2's. I have not measured incoming voltage in at the service entrance (400 amp service) Any thoughts on conduit and feeder size? TIA.
'm kay... it won't be code compliant. that's a given.
what's killing you, is the 120 volt loads. you are going
half a football field.
what's really killing you is the location. you live where
people refrigerate their pool water during the summer.
air conditioning and refers aren't nice to have, they are
something that runs 24/7.
that 50 amp RV plug, when plugged in, WILL have the
AC running. the voltage drop will kill the little AC unit
that is chilling the bunnies. the bunnies will have heat
stroke. the little refrigerator will not like the voltage
drop either, and you'll end up with dead rabbits and
warm beer. you have three chiller loads cycling on
the end of a long line.
run a 220 volt line out there, put a little single phase
transformer to give you 120 volts for the incidental
loads.
even then, 50 amps at 240 volts going 170', will give
you 2.26% voltage drop, using #2 aluminum. copper,
quite honestly, is a waste of money.
i'd use 3 #2's in 1 1/2" pipe, with a #10 copper ground.
but you could direct burial UF cable. save some money.
you only need a 1 1/4" pipe, but it's a long run...... i'd measure
the run with a mule tape, and see if you can get three
wires out of a 500' spool..... it'll be close....