What year/code cycle did stoves go 4 wire?
Thanks,
c2500
Thanks,
c2500
The 1996 NEC section 250-60 was when the change was made .Mobile homes ranges and dryers were required to be four wire prior to the 1996 NEC.
CFR 24 3280.809 (2) Connection of ranges and clothes dryers with 120/240 volt, 3-
wire ratings shall be made with 4 conductor cord and 3 pole, 4-wire
grounding type plugs, or by type AC metal clad conductors enclosed in
flexible metal conduit. For 120 volt rated devices a 3-conductor cord
and a 2-pole, 3-wire grounding type plug shall be permitted.