Brake cleaner is basically the same chemically as lectra clean. But much cheaper.I like spray with electra clean, then cold gav and then a bit of Kopper Shield or Penatrox E. Brake cleaner is a great tip
Kopr Shield gets home before you do, the Penatrox E comes in a squeeze bottle/
Not familar with STL...but if Don recommends it, then it has to be good.
From at least what I’ve always seen and used within our company, we always just wipe clean oil and a good coat of spray gal, BUT we never depend on the raceway as an EGC as we always have one pulled with the circuit. If we was to use the raceway for an EGC I’d take much more precaution.What is everyone using for corrosion protection on field cut threads on rigid conduit, both exposed and buried? Is spraying it with cold galv good enough or should something like Kopr Shield be used?
It is a spec from before I got in the trade at a plastics plant I did a lot of work at. It is a lithium based product and is not near as messy as the copper products....and a lot cheaper.I like spray with electra clean, then cold gav and then a bit of Kopper Shield or Penatrox E. Brake cleaner is a great tip
Kopr Shield gets home before you do, the Penatrox E comes in a squeeze bottle/
Not familar with STL...but if Don recommends it, then it has to be good.
From at least what I’ve always seen and used within our company, we always just wipe clean oil and a good coat of spray gal, BUT we never depend on the raceway as an EGC as we always have one pulled with the circuit. If we was to use the raceway for an EGC I’d take much more precaution.
it doesn't matter if you have pulled a wire type EGC in the metal raceway.You brought up something I failed to mention here, the conduit is not used as EGC it has one installed.
it doesn't matter if you have pulled a wire type EGC in the metal raceway.
The installation rules do not change and it still has to be installed in a manner that would not impede its use as an EGC.
it doesn't matter if you have pulled a wire type EGC in the metal raceway.
The installation rules do not change and it still has to be installed in a manner that would not impede its use as an EGC.
it doesn't matter if you have pulled a wire type EGC in the metal raceway.
The installation rules do not change and it still has to be installed in a manner that would not impede its use as an EGC.
It does stop a bit short of saying that it is conductive. The spec sheet says:I see you also use STL. I’ve only ever used STL8, is there other STL that do actually do help with conductivity and continuity?