Hello! I am planning out the electrical work for my upcoming bathroom remodel.
I have one junction box that I think is going to be busy. It looks like it is going to have:
2x 12/2
2x 14/2 (this could be 1x if needs be)
2x 14/3
1 sconce light (with 18 AWG wiring, so I think it does not count into box fill)
I think this gives me: 4 conductors for the 12/2, 4 conductors for the 14/2, 6 conductors for the 14/3, and 1 conductor for the ground. So 15 total assuming I'm using clamps outside the box. Or 13 if I get rid of one of the 14/2s (which I can do). Hopefully I did that calculation right?
I would like to use a metal, new construction box. My options are... limited. 2020 NEC table 314.16(a) shows 13 12 AWGs allowed in a 4x2 1/8 box. But how do I connect a sconce to a square box? I looked at round mud rings (like Hubbell 757) but the spacing between the two threaded holes on it does not match the spacing on a normal round or octagonal junction box. Is that still an appropriate way of hooking up a sconce? I know sconce lights often have multiple diameters of hole spacings they support so I'm guessing this is OK - but want to double check.
Is this my best path forward, or can you suggest another alternative? I would really like to avoid adding more junction boxes (for purely aesthetics reasons).
Thank you for your assistance!
I have one junction box that I think is going to be busy. It looks like it is going to have:
2x 12/2
2x 14/2 (this could be 1x if needs be)
2x 14/3
1 sconce light (with 18 AWG wiring, so I think it does not count into box fill)
I think this gives me: 4 conductors for the 12/2, 4 conductors for the 14/2, 6 conductors for the 14/3, and 1 conductor for the ground. So 15 total assuming I'm using clamps outside the box. Or 13 if I get rid of one of the 14/2s (which I can do). Hopefully I did that calculation right?
I would like to use a metal, new construction box. My options are... limited. 2020 NEC table 314.16(a) shows 13 12 AWGs allowed in a 4x2 1/8 box. But how do I connect a sconce to a square box? I looked at round mud rings (like Hubbell 757) but the spacing between the two threaded holes on it does not match the spacing on a normal round or octagonal junction box. Is that still an appropriate way of hooking up a sconce? I know sconce lights often have multiple diameters of hole spacings they support so I'm guessing this is OK - but want to double check.
Is this my best path forward, or can you suggest another alternative? I would really like to avoid adding more junction boxes (for purely aesthetics reasons).
Thank you for your assistance!