I was having a discussion with an electrician recently regarding an electric heater installation.
Here?s the installation:
Six-208V, single phase, 2.5kW heaters circuited to six-two pole breakers in a 208V, three phase panelboard installed solely for this project arranged to balance the load across the three phases.
The discussion resulted in a disagreement regarding the total connected load on this panelboard.
I believe that it will be 17.3kW of load, where he felt it would be 15kW. Who's right?
I thought this brain teaser would be an interesting discussion, before I tell you how I got my answer.
[ June 30, 2004, 05:54 PM: Message edited by: ron ]
Here?s the installation:
Six-208V, single phase, 2.5kW heaters circuited to six-two pole breakers in a 208V, three phase panelboard installed solely for this project arranged to balance the load across the three phases.
The discussion resulted in a disagreement regarding the total connected load on this panelboard.
I believe that it will be 17.3kW of load, where he felt it would be 15kW. Who's right?