Note that the PC and timer contacts are in series, which means they both must call for lighting.Well, yeah, but.....
Why not just one or the other?
Why not just one or the other?
Yes, if the homeless can’t see while on the property your customers could be liable for injuries. Not really joking.With the increase in crime, and all the homeless camping out around our warehouses ... all of our Maintenance Contract customers told us to bypass the time clocks and keep them on with the photocell only.
Yes, if the homeless can’t see while on the property your customers could be liable for injuries. Not really joking.
OK completely different subject than the original, but I’m going over these plans and I don’t bid a ton of new commercial, so lighting contactors are pretty unfamiliar to me.
Fully understand what’s contactor is and what it does, but this is a single 20A circuit with some perimeter led lighting around a community building.
So why route it through a contactor?
I can’t even find a single circuit lighting contactor enclosure with a timer and HOA switch. Most are set up for multiple circuits.
Probably boiler plate spec but not a bad idea. If additional lighting is added and the voltage was changed little needs to be done. In many of my cases, the control voltage is from a different circuit than the site lighting.this is a single 20A circuit with some perimeter led lighting around a community building.
So why route it through a contactor?
I always build it myself. On a backboard: Tork timeclock and lighting contactor (in enclosure) offset nippled to a 4x4 trough below them. Lots of time the auto-off-on switch is wanted in the manager's office, not in the electrical room.I can’t even find a single circuit lighting contactor enclosure with a timer and HOA switch. Most are set up for multiple circuits.
Probably boiler plate spec but not a bad idea. If additional lighting is added and the voltage was changed little needs to be done. In many of my cases, the control voltage is from a different circuit than the site lighting.
I always build it myself. On a backboard: Tork timeclock and lighting contactor (in enclosure) offset nippled to a 4x4 trough below them. Lots of time the auto-off-on switch is wanted in the manager's office, not in the electrical room.
-Hal
Ok, no problem. Just don't turn it off.In high crime cities, you need flood lighting 24/7 ... no need for flood lighting to be off at all.
Wrong, photo cell must be powered at all times. That is the biggest mistake a lot of electricians make. When photocell is first powered, it is default on, the lights come on, then go back off. Then at dusk, they turn back on. You have to isolate the time clock contact, which is easily done by moving the clock power wire.1) Install a timeclock
2) Install a photocell
3) The timeclock with trippers turns on at say 3:00 pm and powers the photocell
4) The photocell turns on at sun set.
5) The photocell turns off at 12:00 am midnight from the timeclock