Bugman1400
Senior Member
- Location
- Charlotte, NC
Anybody see any issues with this picture? Specifically, what is the recommended distance between the ground strap and the insulated bus bar? Check out Phase A!
Bingo. Although there are design standards relating to the distance from LIVE conductors to ground, once it is insulated like that, it comes down to what the mfr has tested the equipment at when getting a BIL rating. If they had a ground strap touching the insulation and passed at 60kV BIL, then they passed and there is nothing you can say about it.... I would say at least 6". A good idea would be to check with the manufacturer or use the as built tolerances. ...
This probably does not need to comply with NEC. Manufacturer would specify distance. Is this a collector substation for power generation?
That B phase ground stud should have its insulating cap installed.
34.5Kv? It probably was hipot tested at 80kV
That B phase ground stud should have its insulating cap installed.
Why, if this is really the grounded conductor?
Here is another picture of an adjacent cubicle with a similar issue with the ground strap but, on Phase B. The cause for the investigation is shown in the next picture which shows the obvious cable rupture.
So, since the bus was insulated, the direct contact from the ground strap did not cause an immediate fault. However, the partial discharge over time, eventually breaks down the insulation of both the bus and the cable. Has anybody seen similar issue with the way contractors install MV swgr and MV cables?
The damage looks like corona damage.
The damage looks like corona damage.
Corona is a form of PD. I would not call your situation Corona. Corona is a partial discharge in air. This partial discharge is taking place in the insulation. Eventually the partial discharge will tree it's way through the insulation and arc to the grounded strap.
I am not aware of a camera that will detect partial discharge. A corona camera will help visualize the corona in air. A factory grade PD test is the best way to determine if you have excessive PD. There are EMI detectors that can be used but they give little empirical data.
To reduce corona or PD you need to limit the voltage field imposed at the subject area. Usually you see corona balls or toroids used to mitigate corona. These are used on exposed conductors which utilize only air as insulation. The idea is to increase the surface area and mitigate pointy electrodes. This reduces the voltage field about an area.
First off I would contact the manufacturer. In my opinion to mitigate the PD I would suggest wrapping the problem area with additional insulation and weaken the voltage field by increasing the distance between the ungrounded bus and the ground straps. Consider this to be a bandaid and I would not trust it until gaining approval from the manufacturer and testing the repair.
You may not simply be able to move the cable entry points. If you are lucky you may have a cable loop and enough slack. If not you may need to add a splice.