i was asked to trouble shoot a residental 100 amp panel seems there is no power at the panel only when a load is applied to either phase.
when i arrived onsite (this is a total diy ho rehab) the only conductors connected to the panel where the direct buried feeders from the 100a meter disc.
it tested good for 120v on each phase to net/grd and 240v between both phases i connected a temp rec to a 15a breaker and pluged in a 3 lt rec tester and it showed correct, i then connected a temp socket w/ 60w incadesent in line. if the load is applied to phase a the 120v goes to 0 and open hot shows on rec tester dido with phase b however 120/240v is always available at the load side of the disconect
i changed the disconect 100a breaker, dbl checked all connections/torques and got same effect
leads me to think there is an issue with the direct buried feeders, i can only estimate the feeders are from 5-8 yrs old.
any other ideas? as all are welcomed
when i arrived onsite (this is a total diy ho rehab) the only conductors connected to the panel where the direct buried feeders from the 100a meter disc.
it tested good for 120v on each phase to net/grd and 240v between both phases i connected a temp rec to a 15a breaker and pluged in a 3 lt rec tester and it showed correct, i then connected a temp socket w/ 60w incadesent in line. if the load is applied to phase a the 120v goes to 0 and open hot shows on rec tester dido with phase b however 120/240v is always available at the load side of the disconect
i changed the disconect 100a breaker, dbl checked all connections/torques and got same effect
leads me to think there is an issue with the direct buried feeders, i can only estimate the feeders are from 5-8 yrs old.
any other ideas? as all are welcomed