does the conduit need seals? In this case, the conduit is leaving a C1D2 area going underground- routed through an unclassified area to the same C1D2 area, where it stubs back up.
Agreed- leaving and entering. Working with the inspector on a variance as adding seal offs would simply be protecting each stub up from the same classified area they are in. The "spirit" of the code in this scenario doesn't seem to fit.Technically, you have described two boundaries and Section 501.15(B)(2) would apply. None of the Exceptions would apply.
Does it have to, based on the exception to 501.15(C)?EDIT ADD: The open question now is what fitting to use as a seal fitting because Polywater doesn't meet all the requirements of 501.15(C). Its good stuff though.
both ends of these conduits stub into rated enclosures with sealed and intrinsically safe devices. Was designed to not require seals, but the inspector and engineer have slightly different interpretations of "leaving" or "entering" the classified area.Does it have to, based on the exception to 501.15(C)?
We've also had debates internally whether 501.15(B)(2) exception 4 would apply in this case - is the underground conduit considered 'outdoor' if both risers are outdoors?
CMP 14 has the same problem or did as far as I knowDoes it have to, based on the exception to 501.15(C)?
We've also had debates internally whether 501.15(B)(2) exception 4 would apply in this case - is the underground conduit considered 'outdoor' if both risers are outdoors?
Interesting - i had interpreted the old language to apply to above ground only, but others had not. The new wording makes it clear.Underground and outdoors are not specifically defined NEC terms. As of 2023 the NEC states Exception 4 applies to aboveground installations. (BTW I was the original author for the exception as submitted by API)
Polywater markets and identifies in their literature as meeting 501.15(B) requirements. Although I am sure that some will find that self-evaluation insufficient.Identified is a defined term that doesn't necessarily mean listed or labeled. So what does it mean?
Well maybe/maybe not. That's why Section 500.8(A)(3) was written. CMP 14 couldn't convince CMP 1 to revise the definition of identified to be a bit more liberal sufficiently so we developed suitability based on FedOSHA’s definition of acceptable.Polywater markets and identifies in their literature as meeting 501.15(B) requirements. Although I am sure that some will find that self-evaluation insufficient.