When a project manager/engineer talks of Art 501

Status
Not open for further replies.
Had a project manager who is also the EE for a rewire of a Automotive Repair Structure (I'm choosing my words carefully). The AHJ reviewed the prints prior to bidding and wrote "Note Art 511 of NEC" on every Electrical print. I bid the job in accordance with Art 501. Fixtures & Wiring 18" BFC & 18" AFF. The EE/PM is arguing with me that all the ceiling fixtures & any and all conduit can be and need to be mounted to the ceiling. There is no air circulation systems other then Unit heaters. Anyone have another take?
 