When an indoor AC is fed from outdoor condenser

cppoly

Senior Member
Location
New York
When an indoor AC is fed from outdoor condenser, is the indoor unit considered protected against short circuit / ground fault through the condenser's MOCP?

Or does the indoor unit need to be provided with separate protection for SCGF?

Or, will just a disconnect switch at the indoor unit be ok?

Thanks
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Do you mean a split system that has an indoor unit on the wall? Some jurisdictions want a disconnect switch in the line that connects the indoor unit to the outdoor unit but AFAIC it's totally unnecessary. The indoor unit is protected through the outdoor unit. (The cable that connects the indoor unit has communications on it and the indoor unit may even be DC.)

-Hal
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
When an indoor AC is fed from outdoor condenser, is the indoor unit considered protected against short circuit / ground fault through the condenser's MOCP?

Or does the indoor unit need to be provided with separate protection for SCGF?

Or, will just a disconnect switch at the indoor unit be ok?

Thanks


I agree. The indoor unit gets its protection from the outside unit.
 