Running rigid on a roof going into 24 x 24 can using locknut with gasket on both sides it's insulating the pipe from the can. I imagine this is one instance. What are others? Thank you for your help.
Do you need to bond around sealing locknut's? I don't think so, the teeth still grab the metal.
Running rigid on a roof going into 24 x 24 can using locknut with gasket on both sides it's insulating the pipe from the can. I imagine this is one instance. What are others? Thank you for your help.
and 250.97,98 & 100Look at 250.92.
Running rigid on a roof going into 24 x 24 can using locknut with gasket on both sides it's insulating the pipe from the can. I imagine this is one instance. What are others? Thank you for your help.
If volts are 250V or higher with eccentric and concentric KO’s.
I think there is a nice handy-dandy flow chart somewhere around here that is a great reference for bonding bushings. I don't recall where exactly I saw it.
You never have to use one, but they might be more convenient than other bonding methods. external pipe bonding clamp and external bonding jumper will accomplish the task, but grounding bushing may be preferred over that method.
Could also counter that by saying it may comply with: (4) other listed devices...One could argue that an external bonding jumper with clamp wouldn't comply with 250.92(B) since it's not on the list.