I know the minimum is 100A but when are we not allowed to use the optional method for calculating the apartment load?
220.82(A) says:
This section applies to a dwelling
unit having the total connected load served by a single
120/240-volt or 208Y/120-volt set of 3-wire service or feeder
conductors with an ampacity of 100 or greater.
Can we use this method if we have a combined apartment with 2 panels metered separately? The combined apartment has no wall separating each other. The code in 220.82(A) refers to a single 120/240 or 120/208V feeder but there's 2 feeders in the combined apartment so it's not a single.. Could I do the optional method on each of the panel separately?
220.82(A) says:
This section applies to a dwelling
unit having the total connected load served by a single
120/240-volt or 208Y/120-volt set of 3-wire service or feeder
conductors with an ampacity of 100 or greater.
Can we use this method if we have a combined apartment with 2 panels metered separately? The combined apartment has no wall separating each other. The code in 220.82(A) refers to a single 120/240 or 120/208V feeder but there's 2 feeders in the combined apartment so it's not a single.. Could I do the optional method on each of the panel separately?