I have very little experience with installing gutters.
Based on what I'm reading in the NEC and some EC&M articles, I feel like I'm missing something that allows the use of gutters in more applications. A lot of articles and NEC handbook drawings show horizontal gutters with conduits entering from the top and the bottom. But 314.28 states:
This is an example from the handbook
In the image below I had planned to use a gutter underneath this meter/ATS. I assumed I could run (almost) all these conduits (5 x 1.5", 2 x 3/4") into the bottom of this gutter, then have two conduits (2 x 2") feeding out the back into the panel behind, and one conduit (1 x 1.5") feeding up into the ATS/meter with the generator conductors. But in looking at 314.28 I need a 16.5" tall box. Or am I missing something that would allow less height? Similarly, on the other side of this wall, I wanted to use a gutter that has 2 conduits in the back (2 x 2") of it and 2 on the top (2 x 2"), which by my math needs to be 14" tall.
Based on what I'm reading in the NEC and some EC&M articles, I feel like I'm missing something that allows the use of gutters in more applications. A lot of articles and NEC handbook drawings show horizontal gutters with conduits entering from the top and the bottom. But 314.28 states:
So if those conduits are 2” then the gutter would need to be 16” tall right?“In straight pulls, the length of the box or conduit body shall not be less than eight times the metric designator (trade size) of the largest raceway”. So if those conduits are 2” then the gutter would need to be 16” tall right?
This is an example from the handbook
In the image below I had planned to use a gutter underneath this meter/ATS. I assumed I could run (almost) all these conduits (5 x 1.5", 2 x 3/4") into the bottom of this gutter, then have two conduits (2 x 2") feeding out the back into the panel behind, and one conduit (1 x 1.5") feeding up into the ATS/meter with the generator conductors. But in looking at 314.28 I need a 16.5" tall box. Or am I missing something that would allow less height? Similarly, on the other side of this wall, I wanted to use a gutter that has 2 conduits in the back (2 x 2") of it and 2 on the top (2 x 2"), which by my math needs to be 14" tall.