Charlie I disagree, IMO the term free air means "not in an enclosure" .Originally posted by charlie b:
Conductors that never leave an enclosure, and that are routed throughout the enclosure without any type of raceway, should be treated as being in free air.
Are they really free air inside the enclosure? I would say if they just pass through the enclosure hanging loose you have a good argument. If you end up putting them inside wire duct in the control enclosure I would not consider them free air.Originally posted by tobbink21:
We have conductors in a control enclosure, that measures 84" high 154" long and 24" deep with circulating air. The enclosure is in an electric room that is climate controlled. But simply asking, can we use 310.17 free air table for this application?
And Table 310.17 applies to:Not More Than Three Current-Carrying Conductors in Raceway, [or Not More Than Three Current-Carrying Conductors in] Cable , or [Not More Than Three Current-Carrying Conductors in] Earth (Directly Buried)?
I ?leaned? toward Table 310.16 in my first response and still do unless we know we are only talking about single-conductor cables generally separated from each other.Single-Insulated Conductors ? in Free Air?
Part of the ?conditions of use? is the terminations and Article 110.14(C) still applies.The current, in amperes, that a conductor can carry continuously under the conditions of use without exceeding its temperature rating.
110.14(C)(1) Equipment Provisions. The determination of termination provisions of equipment shall be based on 110.14(A) or (B). Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.16 as appropriately modified by 310.15(B)(1) through (6).
Category Code ?AALZ? is the primary UL investigation category. No product is ?listed? specifically to it, but virtually all products are evaluated under it.Electrical Equipment for Use in Ordinary Locations (AALZ)
?
Appliance and Utilization Equipment Terminations ?
Except as noted in the general Guide Information for some product categories, the termination provisions are based on the use of 60?C insulated conductors in circuits rated 100 A or less, and the use of 75?C insulated conductors in higher rated circuits as specified in Table 310.16 of the NEC. If the termination provisions on equipment are based on the use of other conductors, the equipment is either marked with both the size and temperature rating of the conductors to be used or with only the temperature rating of the conductors to be used.
?
Distribution and Control Equipment Terminations ?
Except as noted in the following paragraphs or in the general Guide Information for some product categories, the termination provisions are based on the use of 60?C ampacities for wire size Nos. 14-1 AWG, and 75?C ampacities for wire size Nos. 1/0 AWG and larger, as specified in Table 310.16 of the NEC.
?