240-5. Overcurrent Protection of Conductors. Conductors shall be pro-
tected in accordance with their ampacity, as given in Tables 310-12
through 310-15, except as follows:
Exception No. 1. Rating of Nonadjustable Overcurrent Protection
of 800 Amperes or Less. When the standard ampere ratings of fuses
and nonadjustable circuit breakers do not correspond with the allow-
able ampacity of conductors, the next higher standard rating may be
used