I had a service call the other day. The elderly HO was shocked when she turned on her disposal with wet hands and touching the S/S sink. She touched the coverplate screw. When I opened the box up, the NM was grounded, but the Leviton switches had no ground screws. The place was built in the mid 70's. I read 11-12 volts to the sink off the switch body. I replaced the switches with grounded ones, and tied in with the grounds in the back of the box.
The wire was #12, and the grounds were #12 also. All the receptacles were properly grounded. I am curious about the transition point when switches were all grounded. Or did some EC have a bunch of old switches siting around?
Thanks,