I've never done this, but have seen it done before so I'm curious if running a grounding wire to a cold water pipe to convert a 2 prong outlet into a grounded 3 prong outlet was ever allowed by the code and if so, which year that was (just so I can sound smart and important with other electricians).
Also, while on the subject, I know if you're going to run a grounding wire to the panel, you might as well run a 12/2 and update the whole circuit, but for argument's sake, would you be allowed to run a 12 awg green THHN wire from one receptacle through the walls and attic back to the panel, assuming of course that it would only stay in that branch circuit and not mixed with others or would it need to be protected with conduit or flex? Again, just for general knowledge and I wouldn't do this myself (though again, I've seen it).
Also, while on the subject, I know if you're going to run a grounding wire to the panel, you might as well run a 12/2 and update the whole circuit, but for argument's sake, would you be allowed to run a 12 awg green THHN wire from one receptacle through the walls and attic back to the panel, assuming of course that it would only stay in that branch circuit and not mixed with others or would it need to be protected with conduit or flex? Again, just for general knowledge and I wouldn't do this myself (though again, I've seen it).