Re: When do the steel beams within a residence require bondi
250.52(A)(2)- requires the metal frame of the bldg. to be used as part of the electrode system 'where effectively grounded'.
As Jim said, 'never' seen it in residential...this is because every steel beam I've ever encountered ( in residential)was an isolated structural member....i.e. not tied into other steel members that created the bldg. framework.
Where this (250.52A2) comes into play (usually) is in commercial/industrial bldgs. where the entire bldg. framework is steel (beams, columns, girders, etc.)...in this type of construction, often times the bolts that secure the columns into place (into huge concrete piers embedded into the monolithic concrete slab) have bonding conductors welded (or cad-welded)to the huge bolts and to the rebar within the slab....thus forming a huge electrode system.
In this scenario there would not likely be a Ufer made available to be part of the electode system ....you would then include the steel columns as part of the electrode system and bond the metal water piping to the bldg. steel. (in the bldgs. I have seen, there have been no ground rods installed and no Ufers made available....so you use the water piping and the bldg. steel).
Hope that wasn't too confusing