When do the steel beams within a residence require bondi

Status
Not open for further replies.
Re: When do the steel beams within a residence require bondi

250.52(A)(2)- requires the metal frame of the bldg. to be used as part of the electrode system 'where effectively grounded'.

As Jim said, 'never' seen it in residential...this is because every steel beam I've ever encountered ( in residential)was an isolated structural member....i.e. not tied into other steel members that created the bldg. framework.

Where this (250.52A2) comes into play (usually) is in commercial/industrial bldgs. where the entire bldg. framework is steel (beams, columns, girders, etc.)...in this type of construction, often times the bolts that secure the columns into place (into huge concrete piers embedded into the monolithic concrete slab) have bonding conductors welded (or cad-welded)to the huge bolts and to the rebar within the slab....thus forming a huge electrode system.

In this scenario there would not likely be a Ufer made available to be part of the electode system ....you would then include the steel columns as part of the electrode system and bond the metal water piping to the bldg. steel. (in the bldgs. I have seen, there have been no ground rods installed and no Ufers made available....so you use the water piping and the bldg. steel).

Hope that wasn't too confusing
 
Re: When do the steel beams within a residence require bondi

Just out of curiosity, are you dealing with a real-world problem, or just an academic discussion?
 
Re: When do the steel beams within a residence require bondi

I've watched steel become more of a part of residential construction over years as building code reqm's change. The most I have seen is two columns and one beam conected together. They were not exposed as in 250-104(d) so did not require bonding. It was decided that the requirements of 250-50(b) were not met and it did not need to be bonded to the grounding electrode system.


We have found there is always have a footing available somewhere in a commercial bldg for the UFER and the engineer usually calls for one. i've seen some pretty extravagantly designed UFER systems. Such as two 50 foot lengths of 500kcmil each way in the footing.
 
Re: When do the steel beams within a residence require bondi

just an academic discussion

[ August 13, 2004, 08:16 AM: Message edited by: dabent ]
 
Re: When do the steel beams within a residence require bondi

How about if the steel is 'effectively' grounded, and one uses it for the purpose of 250.53(D)(2) instead of driving two ground rods.

The question that begs to be answered now is; what is effectively grounded?

Pierre
 
Re: When do the steel beams within a residence require bondi

Originally posted by websparky:
Building steel is never a grounding electrode.
Dave, on the upper floors of steel frame high-rise building's, steel is the only electrode availible for SDS.
 
Re: When do the steel beams within a residence require bondi

Dave
There are a lot of new homes being built around here, and most of them are quite large - with steel throughout the basement. I have been telling the contractors to have the GC use a 'J' bolt in the pier, bonded to the rebar, that the lolly column is on and then I consider it 'effectively' grounded, using it as a supplemental grounding electrode. I personnally believe it is a better ground than any ground rod in our area.

Pierre
 
Re: When do the steel beams within a residence require bondi

Pierre I do not see how you can tell them to do that, IMO you can only ask for that.

What code section gives you that power?

Bob
 
Re: When do the steel beams within a residence require bondi

Bob
You are right...I did not write that post correctly. What I meant is, I tell the EC that they can use the steel as the Supplemental ground, avoiding driving ground rods.
There are many areas here that it is very, very difficult to drive ground rods.


One day I will learn how to write in a more clear manner... until then thanks for keeping me on my toes. Remember, I was a contractor for years, and remember how difficult sometimes driving ground rods can be. :D

[ August 15, 2004, 12:06 PM: Message edited by: pierre ]
 
Re: When do the steel beams within a residence require bondi

Pierre I doubt you need anyone to keep you on your toes. :)

I think your suggestion is an excellent one and I would do it that way if the opportunity presented itself. :)

Bob
 
Re: When do the steel beams within a residence require bondi

Pierre,

In my area, the steel columns set on top of a concrete pad, usually 4-6 inches below the finished concrete floor. Some of the steel beams span from basement wall to basement wall with no columns. The ones with columns may offer some contact with the earth for grounding purposes but the earth under the basement would have to be some-what moist to be effective.

In either case, I would not consider the steel to be a good electrode. However, if one were to bond the steel......it wouldn't hurt anything. Does the steel need to be bonded? That would be a judgement call for the AHJ.
 
Re: When do the steel beams within a residence require bondi

In Canada we would require the steel beam to be bonded if there was a possibility of it becoming energized. Possibility is if there are any nmd cables located in the proximity that could come in contact with the beam.
Jafro
 