when do you need a fire supression system?

Status
Not open for further replies.

megloff11x

Senior Member
NFPA 79 does not mention fie suppression systems. NFPA 86 section 13.1 notes that "a study shall be conducted for fixed or portable fire protection systems for ovens, furnaces, and related equipment. This determination shall be based on a review of the fire hazards associated with the equipment. Were determined to be necessary, fixed or portable fire protection systems shall be provided."

Is there further guidance provided in other NFPA codes?

I've worked on machines where other industry standards required fire suppression, even when the machine had no heaters or significant fuel sources.

Matt
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: when do you need a fire supression system?

The only one I ever saw on a machine was a CNC machining center that was using ethanol as a cutting fluid.
 