C conmgt Senior Member Location 2 Phase Philly Apr 2, 2013 #1 I'm seeing these available in both insulated and non-insulated in sizes up to 4"
iwire Moderator Staff member Location Massachusetts Apr 2, 2013 #2 Never specifically code required, it is just a design decision. You can always use a bushing instead when the conductors are 4 or larger.
Never specifically code required, it is just a design decision. You can always use a bushing instead when the conductors are 4 or larger.
kwired Electron manager Location NE Nebraska Occupation EC Apr 2, 2013 #3 I don't think it ever has to have insulating throat. Having an insulating throat may relieve the need of an additional insulating bushing when required.
I don't think it ever has to have insulating throat. Having an insulating throat may relieve the need of an additional insulating bushing when required.
S Strathead Senior Member Location Ocala, Florida, USA Occupation Electrician/Estimator/Project Manager/Superintendent Apr 2, 2013 #4 Or another possible way to answer this is, "When the electrical Specifications require it." That is usually where you will see the requirement.
Or another possible way to answer this is, "When the electrical Specifications require it." That is usually where you will see the requirement.