I am having an opinion difference with some on PPE requirements and when they apply.
EX: An MCC bus (line side of bucket breakers) has an AF category of 2. The load side of the bucket breaker is category 0. The bucket breaker is open (breaker off) and the electrician is doing work inside the bucket. The load side of the bucket breaker is de-energized and there is no exposed bus (which is categeory 2). However, the line side lugs of the breaker are live.
Does the electrician have to wear category 2 PPE?
I know very well that an arc flash can occur, even if the worker does nothing to cause it. How far do we go in requiring our people to wear proper PPE if there is no exposed bus and the "could happen" may be a long shot?
Is there documentation I can use to back this up?
I always err on the conservative side for these issues. But sometimes, too much protection can be harmful as well. Do I go too far in requiring category 2 PPE when the only exposed live parts are the line side breaker lugs?
I would love some thoughts on this one.
EX: An MCC bus (line side of bucket breakers) has an AF category of 2. The load side of the bucket breaker is category 0. The bucket breaker is open (breaker off) and the electrician is doing work inside the bucket. The load side of the bucket breaker is de-energized and there is no exposed bus (which is categeory 2). However, the line side lugs of the breaker are live.
Does the electrician have to wear category 2 PPE?
I know very well that an arc flash can occur, even if the worker does nothing to cause it. How far do we go in requiring our people to wear proper PPE if there is no exposed bus and the "could happen" may be a long shot?
Is there documentation I can use to back this up?
I always err on the conservative side for these issues. But sometimes, too much protection can be harmful as well. Do I go too far in requiring category 2 PPE when the only exposed live parts are the line side breaker lugs?
I would love some thoughts on this one.