I have been in a debate with our EOR about when we will need to have a neutral on our solar PV sites. I understand that there are inverters that may need a neutral for sensing purposes and can be downsized to the EGC as per 705.95(B), and some inverters don't need a neutral at all. What we are running into is that we have 3ph 3W circuits running out to the AC Combiner panels and that wouldn't be a problem until we have Data Acquisition loads on that panel board that are 2ph Line to Line. While this load is small it will be unbalancing the phases and in my opinion would necessitate a neutral run to this panel. I have been scouring the code trying to find when a neutral conductor becomes a requirement. I noticed 220.61 gives a little more information on this but not a clear cut answer on when it would be a requirement. Are there any other NEC articles I could reference for neutrals? In the past I have worked on other projects that have had more significant unbalanced loads (tracker motors, lighting, ev chargers etc.) and feel like those would most certainly require the neutral but here because the unbalanced load is fairly light (1-2A) I am not sure what the impact would be if we did not install a neutral.