When is a panel upgrade required?

Merry Christmas

JoeNorm

Senior Member
Location
WA
I have some new circuits to add at a residence with an older Byant panel with the multicolored breakers. If I am not mistaken they are comparable with BR breakers. All the single pole breakers are twinned already so if I want more space i'll have to start using quads.

Where is the line of "you need a new panel"? Around here labor rates are quite high, so panel swaps are pretty expensive. If the customer is on a tight budget it can be hard to tell them they need a $5K upgrade when the job might be able to be accomplished with some quads, doubling up circuits, etc.

So where is the line?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
There is a difference between the amount of load and the quantity of loads.

If you need more circuits, you only need to add a sub-panel.

I you need more load capacity, you need a service upgrade.

So, you have to do a present-load and added-load calcs.

BTW, quads are merely multi-pole twins, so won't add space.
 

JoeNorm

Senior Member
Location
WA
Thanks. I need space. The service is 200 Amp.

I was referring to a breaker that has two 2-pole breakers. So combining a couple of standard 2-pole breakers certainly gives you two free spaces

I suppose a subanel is a fine idea and I can let sleeping dogs lie with the old panel
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Thanks. I need space. The service is 200 Amp.
Okay, not enough additional load to warrant load calcs.

I was referring to a breaker that has two 2-pole breakers. So combining a couple of standard 2-pole breakers certainly gives you two free spaces
Aha, you meant as replacements. I dislike doubling up higher circuits.

I suppose a subanel is a fine idea and I can let sleeping dogs lie with the old panel
Yes, much, much, much easier to fish new circuits into than an over-full existing panel.

If you need the space for your sub's feeder, move two smaller circuits to the new sub.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
BTW, quads are merely multi-pole twins
It's not quite that simple.
Quads are two twins *with circuit limiting for notched buss*

If every buss space in the panel has a notch, fill it up with quads.

But if it's a non-ctl panel, you have to do a certain field modification to the quads to make them fit
 