When is a rubber mat required?

Status
Not open for further replies.

bmense

Member
In taking my master electrical examine there was a question that asked, I'm paraphrasing, "What is the voltage level minimum that requires a rubber mat to be placed at the work area?"

I have looked both in the OSHA and NEC books and can not find the instance where this is covered. Any help on this would be appreciated. I'm looking for both the location of the information and the answer.

Thanks a bunch.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: When is a rubber mat required?

250.174(C), 430.133, 535.20(G) and 640.45 are the only places that the code requries nonconductive mats or matting.
Don
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: When is a rubber mat required?

Originally posted by don_resqcapt19: 250.174(C), 430.133, 535.20(G) and 640.45 are the only places that the code requires nonconductive mats or matting.
The first two articles you mention both cite the 150 Volt level, the third does not exist, and the fourth relates to using a mat to cover wires along a floor, to avoid a trip hazard. I would have to agree that an exam would be looking for the answer of 150.
 

bmense

Member
Re: When is a rubber mat required?

Just wanted to drop a note to the kind folks that took the time to respond to my question. The question was once again on the exam and this time I got it right with out guessing.

I passed my exam with an 85% and I owe part of my success to you all!

Thanks!
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: When is a rubber mat required?

Thanks, I see it now. That one also relates to using a mat to cover wires along a floor, to avoid a trip hazard.
 