Re: When is a smoke detector required in garage per NFPA
NFPA 72
11.5.1* One- and Two-Family Dwelling Units.
11.5.1.1 Smoke Detection. Where required by applicable laws, codes, or standards for the specifice occupancy, approved single- and multiple-station smoke alarms shall be installed as follows:
(1) In all sleeping rooms
Exception: Smoke alarms shall not be required in sleeping rooms in existing one- and two-family dwelling units.
(2) Outside of each separate sleeping area, in the immediate vicinity of the sleeping rooms
(3) On each level of the dwellling unit, including basements
Exception: In existing one- and two-family dwelling units, approved smoke alarms powered by batteries shall be permitted.
5.7.1.8* Unless specifically designed and listed for the expected conditions, smoke detectors shall not be installed if any of the following conditions exist:
(1) Temperature below 0 degrees Centigrade(32 F)
(2) Temperature above 38 degrees Centigrade (100F)
(3) Relative humidity above 93 percent
(4) Air velocity greater than 1.5 m/sec (300 ft/min)
110.3(B) requires us to follow listing and labeling.
From BRK's website:
HEAT ALARMS
Heat alarms can be installed in areas not generally suitable for smoke alarms, including garages and attics.
Pierre