Are there specific cases where the cable ampacities in table 310.15(B)(17) can be used? My understanding has always been that based on 110.14 termination temperature ratings dictate that we are to use ampacities listed in 310.15(B)(16) regardless of application. 110.14(C) says that 310.15(B)(16) should be used and appropriately modified by 310.15(B)(17) (Not sure what that modification part intends to convey)
I see the ampacities in 310.15(B)(17) applied a lot in cable tray applications with the basis of cables in "free air" I've always been confused in these cases where the termination temperature limitation comes into play in these cases? Can this table only be applied if the cable terminations are also in "free air" or is this table applicable when cables are in free air and termination is in an enclosure (panelboard, switchgear etc...)?
Thanks
I see the ampacities in 310.15(B)(17) applied a lot in cable tray applications with the basis of cables in "free air" I've always been confused in these cases where the termination temperature limitation comes into play in these cases? Can this table only be applied if the cable terminations are also in "free air" or is this table applicable when cables are in free air and termination is in an enclosure (panelboard, switchgear etc...)?