BCSElectric
Member
- Location
- Orlando
- Occupation
- Electrician
I replaced the inside and outside panels but not the 3 wire feeder between. The homeowner wanted the federal Pacific panels changed but not the wire(to save costs). The inspection failed. The AHJ said that the cable had to be changed to 4 wire when both panels are changed. I have done the same in other jurisdictions with no issues(neutral and ground bonded on both panels). Is there a requirement in Florida building code or NEC to replace with 4 wire in this situation? An inspector in another jurisdiction told me it’s grandfathered in and cannot be required to be replaced Unless it is a 25-50% remodel. Can it be required without a reference to prove his opinion?