Do you think the rules in 430.52 for sizing SCGF protection multiple motors to the same branch circuit is incorrectly used and overused? This lets your size the branch circuit breaker to largest motor's SCGF device + the sum of the remaining FLCs not exceeding the largest motor's breaker size. But, reading the rule it seems like you can only use this formula for listed group installations, right? This general rule does not apply if you're putting two exhaust fans on one circuit let's say or putting two evaporators on one circuit, etc. Right??