When is PVC not allowed indoors?

cppoly

Senior Member
Location
New York
Looking at section 352.12 - I don't see indoors in the uses not permitted section. Yet, why do I feel like PVC is never installed inside commercial buildings ? Are there other sections of code that prohibit PVC to be used ?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Looking at section 352.12 - I don't see indoors in the uses not permitted section. Yet, why do I feel like PVC is never installed inside commercial buildings ? Are there other sections of code that prohibit PVC to be used ?
Its use might be restricted by the fire code. It makes some noxious smoke when it burns.

Or it might just be tradition or design choices. Especially in smaller sizes it does not hang as straight as metal and does not look as nice.

It also flexes more from thermal effects.
 

jap

Senior Member
Occupation
Electrician
I'd be leaning towards the fire code thing also but am curious myself.

JAP>
 

cppoly

Senior Member
Location
New York
All good answers. Basically less efficient and harder to install. Although, I like the fire code comment and need to investigate this one. Anyone know if PVC is prohibited in NYC or NYS?
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
Many commercial spaces use return air plenums above hung ceilings so PVC cannot be used there.
Lots of states haven't allowed new systems like that to be installed. WA hasnt allowed that style of plenum in new work for 20 years or so. Same as using a joist bay as a plenum which has fallen out of favor and been removed as an option for many.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
In California you can't use the building structure as a supply or return, it has to be a ducted system.

The California 2005 Building Energy Efficiency Standards (Title 24, Part 6). "Building spaces such as cavities between walls, support platforms for air handlers, and plenums defined or constructed with materials other than sealed sheet metal, duct board, or flexible duct must not be used for conveying conditioned air including return air and supply air. The practice of using drywall materials as the interior surface of a return plenum is not allowed".
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
In California you can't use the building structure as a supply or return, it has to be a ducted system.

The California 2005 Building Energy Efficiency Standards (Title 24, Part 6). "Building spaces such as cavities between walls, support platforms for air handlers, and plenums defined or constructed with materials other than sealed sheet metal, duct board, or flexible duct must not be used for conveying conditioned air including return air and supply air. The practice of using drywall materials as the interior surface of a return plenum is not allowed".
California wont fix broken intake duct, stepped on, or punctured, so legionnaires, asbestos, black mold, vermin feces, & smoldering toxins may still get occupants sick.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I installed PVC in ug water flow meter vaults and in above ground chlorination rooms. It’s much slower to install than EMT, and while pre bent elbows can be used, they have a diy look.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I installed PVC in ug water flow meter vaults and in above ground chlorination rooms. It’s much slower to install than EMT, and while pre bent elbows can be used, they have a diy look.
That’s why it’s not used so much in commercial. Looks like a hack or romex jockey jockey installed it. Along with it not looking good without a whole lot of strapping!
 

cppoly

Senior Member
Location
New York
Thanks to @ron for posting this in another thread, regarding NYC specifically:

On pg 47 there's an ammendment to article 352 that prohibits PVC in any residential building or dwelling not exceeding three floors above grade.

In NYC, looks like PVC is permitted in residential buildings above 3 stories or commercial buildings (of any height) within non-plenum walls, floors, and ceilings that have a one hour rated assembly. It looks like it's only prohibited in plenum spaces and OK everywhere else indoors (excluding the Uses Not Permitted section 352.12: hazardous locations, etc.).
 