I was called because a vacuum cleaner had been tripping both breakers for the past 6 months. It was clear the vacuum was the problem so I replaced both breakers due to excessive use and separated them while I was at it.
As I was leaving they mentioned that something caused a trip in the master bedroom that caused the guest bedrooms to trip as well. They couldn't remember specifics. I ensured that the recep in question was indeed on the proper circuit and everything appeared to be wired correctly. With no way to duplicate the problem, or any other information, I told them if it happens again to make careful note of everything that was running at the time and call me back.
They just called. A 1500W space heater used in the master will reliably trip both breakers. Of course it's tripping the master. That circuit is way underpowered and the other loads they mentioned put it over capacity. But why is it tripping the other breaker?
I used to work for the company that wired that house. I know the home runs are probably a twisted clump of wires with little to no separation. That makes me wonder about induction. I'm still learning about the inner workings of AFCIs but I was thinking the high current from one could induce enough current in the other wires to cause it to open.
Any thoughts are greatly appreciated.
Thanks. =)
As I was leaving they mentioned that something caused a trip in the master bedroom that caused the guest bedrooms to trip as well. They couldn't remember specifics. I ensured that the recep in question was indeed on the proper circuit and everything appeared to be wired correctly. With no way to duplicate the problem, or any other information, I told them if it happens again to make careful note of everything that was running at the time and call me back.
They just called. A 1500W space heater used in the master will reliably trip both breakers. Of course it's tripping the master. That circuit is way underpowered and the other loads they mentioned put it over capacity. But why is it tripping the other breaker?
I used to work for the company that wired that house. I know the home runs are probably a twisted clump of wires with little to no separation. That makes me wonder about induction. I'm still learning about the inner workings of AFCIs but I was thinking the high current from one could induce enough current in the other wires to cause it to open.
Any thoughts are greatly appreciated.
Thanks. =)