Oops, sorry...I was in a rush when I posted the previous entry and didn't give the backstory to the problem which prompted me to ask the question in the first place. We have a couple of guys on our crew, one in particular that will run 12/2 MC for long distances and never even consider VD. On one occasion, he ran a 12/2 ckt for convenience receptacles at least 345'. I mentioned to him that he was going to have a VD, after which and he used his meter to test the last receptacle; the meter read 115v, the supply PNL read 117v (which is where I came up with that voltage btw). His response was that it was only a 2 volt drop and well within the range. I in turn responded that it was a meter, not a load and to apply I is to decrease E. Two weeks later, I receive a call that a ckt wasn't working. The facilities manager tells me that the housekeeping woman complained about her 12I vacuum not working on the East side of the building on the convenience receptacles...the exact receptacle where I had the argument with our guy about VD. My rule is if I'm running convenience ckts that I always make sure that at any point you can plug in a 12I vacuum or dehumidifier in case of flood, etc. and it works...but maybe that's just me.