When the plans show....
I was wondering if he said he could use it for lighting. Hmmm.
Nope!
Can you imagine a wire nut coming loose and 120 or 277 Volt to the ceiling grid work!
One of our jobs saw a set of plans, electrical = 1 centered smoke, hvac= 1 centered vent
nobody bothered to overlay them
~RJ~
Bond the grid to the box.
Did a hospital remodel when the "cloud" and angled ceilings rage started, the Arch. had a tapered ceiling that at about half way would require us to core the floor above to fit the fixtures. In the meeting just couldn't make them understand so just waited for the Carps to put up the grid and hung a couple fixtures below the grid tight to the upper deck, they got he idea then.
.... the light goes in the middle of the room........
.... and a main tee runs right down the middle..........
No way you should have voltage in this. Does somebody get killed because you lit the grid up? This is a no-no...
The idea is fantastic. But, the chances of the grid going live, and this is not an approved method is putting you in some big liability issues, IMHO. This box is already tight, so you have space issues with the wiring and scotch locks. Ok, someone will say, bond the grid. And how do we do that as an approved means? And Gavin Industries with their box clearly states this is a low voltage installation. They know they could never get this approved for voltages above 50.
How is the grid not already bonded to the same structure that the box is anyway?
A drop ceiling is floating in the breeze. No way it would be considered bonded if something like a hot wire touches and attempts to trip a breaker. I would think it could become hot and no ones know it until someone touches it and a better grounding source.
where did you see that it was for low voltage uses? I just seen on there site it was for light fixtures,fans,etc
When you go to the site URL that's posted, click on the video on the same page and listen to what he is saying as he installs it. It's around the .50 second mark. The guy clearly states it's for Fire alarm and Cameras. I went there looking for this. No way the drop ceiling could ever be bonded in a way that if there was a fault in this box could it be relied on to trip the breaker. At least the drop ceilings I have dealt with.
Please post where Galvin is saying it's for lighting, fans.
Thanks,
Gary
...The guy clearly states it's for Fire alarm and Cameras....
No, he doesn't. Don't paraphrase. He says it's not recommended for high voltage, and is usually for security and fire alarm. Significant difference that doesn't yet say not to do it.
That said, your point is valid and I could see it being an issue, but perhaps if one DOES have a bonded grid, it would be permissible.
Interestingly, one of the reviews that they have posted on that page is from someone that used it for track lighting.
OK, I will let this dog lie... It's noted where I stand on this installation.
Gary