Salvador Santos
Member
- Location
- Bahrain
Good day!
I have some questions regarding the Articles 250.24(C) and 250.32(B). I'm on an ongoing project that is required to build an independent power source to a military camp. We will have 6x1.25MVA Gensets, 380V, 3Ph feeding 6x1.25MVA Step up Transformer 380V Delta/15kV Wye then to substations Stepdown transformer 15kV Delta/380V wye. Our substation will have its own grounding system composed of 3 Grounding rods bonded together by 95mm2 grounding electrode. Our buildings which will have their own MDP will be fed by the substation by phase conductors, neutral conductor and grounding electrode.
Our designers sized the feeder grounding electrode based on 250.32(B), following the size of the ground cables from Table 250.11. In my understanding it should fall under Article 250.24(C) and the grounding electrode sizes should be based on Table 250.66.
My question are:
1. Where does the feeders for each building falls?
2. Should we not consider our cable us service feeders?
3. When do we consider our MDP and Sub DP as equipment or service equipment.
4. Generally, I'm just confused between 250.24(C) and 250.32(B)
Thanks a lot in advance.
I have some questions regarding the Articles 250.24(C) and 250.32(B). I'm on an ongoing project that is required to build an independent power source to a military camp. We will have 6x1.25MVA Gensets, 380V, 3Ph feeding 6x1.25MVA Step up Transformer 380V Delta/15kV Wye then to substations Stepdown transformer 15kV Delta/380V wye. Our substation will have its own grounding system composed of 3 Grounding rods bonded together by 95mm2 grounding electrode. Our buildings which will have their own MDP will be fed by the substation by phase conductors, neutral conductor and grounding electrode.
Our designers sized the feeder grounding electrode based on 250.32(B), following the size of the ground cables from Table 250.11. In my understanding it should fall under Article 250.24(C) and the grounding electrode sizes should be based on Table 250.66.
My question are:
1. Where does the feeders for each building falls?
2. Should we not consider our cable us service feeders?
3. When do we consider our MDP and Sub DP as equipment or service equipment.
4. Generally, I'm just confused between 250.24(C) and 250.32(B)
Thanks a lot in advance.