- Location
- Chapel Hill, NC
- Occupation
- Retired Electrical Contractor
This was a question posted on a forum and I was curious about. As I read it I thought the disconnect is sized by 430.251(B) and the conductor by 430.7(B)???? But I don't think so now.... 430.6 states to use 430.247, 248, 249, 250 for all motors other than low speed, high torque or multispeed. I don't see anything that states what to do with Code Letter. Would you really just use 430.250 for conductor size.
This would mean a disconnect at 725 amps and a conductor at 101 amps? Yes, No
This would mean a disconnect at 725 amps and a conductor at 101 amps? Yes, No
Using Table 430.7(B) I have a question about whether 430.251(B) should be used to determine Locked Rotor Current (LRC) for fire pumps. At the end of the table it gives some specific places the table can be used: "For use only with 430.110, 440.41. 455.8(C)." Do we use this table for the LRC on motors and in the case fire pump or do we use Table 430.7(B)? I was told that we don't use 430.7(B) to calculate motor LRC and must use 430.251(B). This does not seem right. The 430.251(B) LRC for the fire pump motor (480V 100HP Code letter C) is 725A and the Table 430.7(B) calculated maximum current is 480A. Which one is right? This makes a big difference in my mind.