I didn't see the thread that Dennis started, but my reaction to this question is that it cannot happen. Listed equipment is outside the scope of the NEC, and therefore cannot violate the NEC.What happens when a piece of UL equipment violates the NEC?
Bring this to the attention of the listing agency. There are times that listed equipment is manufactured in violation of the UL standards that there are suppose to be listed to.
This exact issue was brought up at an inspectors forum that I attended and the UL representatives said that they would like to hear about these type of situations.
Chris
I didn't see the thread that Dennis started, but my reaction to this question is that it cannot happen. Listed equipment is outside the scope of the NEC, and therefore cannot violate the NEC.
Then why did they permit electronic switching devices to use the EGC as a current carrying conductor? That permission from UL to use the EGC in violation of the NEC rules is why we now have to run a grounded conductor to switches....UL isn't about to 'violate the NEC.' ...
Any current on the EGC, other than fault current, is objectionable to me. If you use the EGC as a normal current carrying conductor, is it still an EGC? I think not.Don, the NEC never, as best I can tell, forbade the use of the ground wire as a conductor. All the NEC ever banned was 'objectionable' current over it.
Sure, there was some debate at the time, but back then about the only thing that used the ground wire were some illuminated switches. It was also seen as inevitable with certain electronics that there would be some current on the ground wire. Define 'objectionable.'
Enter the new millennium, where various save-the-world types want to mandate all manner of automatic switching. Suddenly, we're looking at a lot more current going over that wire. Plus, we have all those power quality concerns that we were blissfully ignorant of even in 1980.
I don't think the NEC even yet bans current over the EGC; you're just required to run the neutral to the residential switch boxes. Thus, the UL standards are still in conformance with the NEC.
Though I expect that to change ....... that is, I expect the standards to change, in tandem with the NEC changing.
Grounding Conductor, Equipment (EGC). The conductive path installed to connect normally non?current-carrying metal parts of equipment together and to the system grounded conductor or to the grounding electrode conductor, or both.
What happens when a piece of UL equipment violates the NEC?
For example, we have roof top HVAC units with the wiring inside the air stream (plenum) that is covered in ENT. This to me would violate 2008 NEC 300.22 (B) and (C).
UL and other NRTL's do not go looking for products to inspect, the makers of products come to them. Any listing they give to a product is based on the equipment that was evaluated. They have no way of knowing if there was a change made to a product unless it was presented to them for re-evaluation.
Likewise USDA inspects meat and dairy processing facilities. That does not guarantee that once they approve a plant and leave that things will not change once they are gone. Unlike UL they will come back even if not invited back.