Hello, I am a Korean participating in electrical construction work in the United States. I am planning to install power cables in a cable tray, but I do not understand exactly which NEC regulations to apply.
I am planning to install a 500kcmil, 90°C rated, single-core copper cable on a cable tray. In this case, I am wondering whether I should apply Table 310.15(B)(17) or Table 310.15(B)(16)
Table 310.15(B)(17) shows the allowable ampacity for cables installed in free air, but it does not mention anything about cable tray installations. When I ask AI, it suggests referring to Table 310.15(B)(16). However, I understand that Table 310.15(B)(16) applies to the allowable ampacity for multiconductor cables.
I would appreciate it if you could clarify whether Table 310.15(B)(16) indicates the allowable ampacity for multiconductor cables as well as for single-conductor cables in steel conduits, cable trays, and cable ducts, or if it only applies to the allowable ampacity for multiconductor cables
I am planning to install a 500kcmil, 90°C rated, single-core copper cable on a cable tray. In this case, I am wondering whether I should apply Table 310.15(B)(17) or Table 310.15(B)(16)
Table 310.15(B)(17) shows the allowable ampacity for cables installed in free air, but it does not mention anything about cable tray installations. When I ask AI, it suggests referring to Table 310.15(B)(16). However, I understand that Table 310.15(B)(16) applies to the allowable ampacity for multiconductor cables.
I would appreciate it if you could clarify whether Table 310.15(B)(16) indicates the allowable ampacity for multiconductor cables as well as for single-conductor cables in steel conduits, cable trays, and cable ducts, or if it only applies to the allowable ampacity for multiconductor cables