What was the first year The code book started requiring the general purpose receptacles in a kitchen be dedicated and not connected to other areas?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Got to go back farther than 1965...


From the 1965 NEC
Article 220-3 (b) Receptacle circuits, Dwelling Occupancies
For the small appliance load in kitchen, laundry, pantry, family room, dining room and breakfast room of dwelling occupancies, two or more 20 ampere branch circuits in addition to the branch circuits specified in Section 220-3(a) shall be provided for all receptacle outlets in these rooms, and such circuits shall have no other outlets.
Receptacle outlets supplied by at least two appliance receptacle branch circuits shall be installed in the kitchen.
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Got to go back farther than 1965...


From the 1965 NEC
Article 220-3 (b) Receptacle circuits, Dwelling Occupancies
For the small appliance load in kitchen, laundry, pantry, family room, dining room and breakfast room of dwelling occupancies, two or more 20 ampere branch circuits in addition to the branch circuits specified in Section 220-3(a) shall be provided for all receptacle outlets in these rooms, and such circuits shall have no other outlets.
Receptacle outlets supplied by at least two appliance receptacle branch circuits shall be installed in the kitchen.
NIce!!! good job, thank you. 55 years ago.
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
I do a lot work in condos constructed in 1941. The original four circuits included a 20 amp circuit for the kitchen and dining room and same for fridge.
 

480sparky

Senior Member
Location
Iowegia
Got to go back farther than 1965...


From the 1965 NEC
Article 220-3 (b) Receptacle circuits, Dwelling Occupancies
For the small appliance load in kitchen, laundry, pantry, family room, dining room and breakfast room of dwelling occupancies, two or more 20 ampere branch circuits in addition to the branch circuits specified in Section 220-3(a) shall be provided for all receptacle outlets in these rooms, and such circuits shall have no other outlets.
Receptacle outlets supplied by at least two appliance receptacle branch circuits shall be installed in the kitchen.


1959.

There is a 'ramp-up' to the requirement before that. In prior years, 1500va was required to be in the load calculations, but no SABCs were specified.
 