What was the first year The code book started requiring the general purpose receptacles in a kitchen be dedicated and not connected to other areas?
NIce!!! good job, thank you. 55 years ago.Got to go back farther than 1965...
From the 1965 NEC
Article 220-3 (b) Receptacle circuits, Dwelling Occupancies
For the small appliance load in kitchen, laundry, pantry, family room, dining room and breakfast room of dwelling occupancies, two or more 20 ampere branch circuits in addition to the branch circuits specified in Section 220-3(a) shall be provided for all receptacle outlets in these rooms, and such circuits shall have no other outlets.
Receptacle outlets supplied by at least two appliance receptacle branch circuits shall be installed in the kitchen.
Got to go back farther than 1965...
From the 1965 NEC
Article 220-3 (b) Receptacle circuits, Dwelling Occupancies
For the small appliance load in kitchen, laundry, pantry, family room, dining room and breakfast room of dwelling occupancies, two or more 20 ampere branch circuits in addition to the branch circuits specified in Section 220-3(a) shall be provided for all receptacle outlets in these rooms, and such circuits shall have no other outlets.
Receptacle outlets supplied by at least two appliance receptacle branch circuits shall be installed in the kitchen.