When/why does the Main Disconnect SW need to be fused for a cabinet with multiple loads?

emiller233

Senior Member
Location
pittsburgh, pa
Occupation
Controls-Automation engineer
When does the Main Disconnect sw need to be fused for a cabinet with multiple motors? I'm looking thru the NEC, but not sure where to look...
there will be an enclosure with 2 motors and a small control power transformer

480VAC, 3-phase supply
  • NEC 70 table 430.52 says 175-225% for time delay fuses
    • 300HP, 361FLA, Fuse size = 631A … 812.25A
      • motor will be on a soft starter
    • 40HP, 52FLA, Fuse size = 91A … 117A
      • DOL motor starter
    • 750VA XFMR single phase, 2A fuses on the primary side
      • powers control circuit
I think I can use a 400A main disconnect switch on this enclosure. The customer will be responsible for providing upstream circuit protection for this enclosure. what section of code would this be detailed in..?
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
Part 3 & 4 of 430.

Multi-motor combination loads overload protection (part 3) and ground fault protection (part 4).

A fused disconnect switch will only be required when it is being used to protect that switchboard.

You will need a disconnect for each motor. Potentially, each one will have a fused disconnect or will have a rated breaker in the switchboard. Depends on how each motor is being individually protected / disconnected.

The disconnecting means can not be less than 430.115
 