emiller233
- pittsburgh, pa
- Controls-Automation engineer
When does the Main Disconnect sw need to be fused for a cabinet with multiple motors? I'm looking thru the NEC, but not sure where to look...
there will be an enclosure with 2 motors and a small control power transformer
480VAC, 3-phase supply
- NEC 70 table 430.52 says 175-225% for time delay fuses
- 300HP, 361FLA, Fuse size = 631A … 812.25A
- motor will be on a soft starter
- 40HP, 52FLA, Fuse size = 91A … 117A
- DOL motor starter
- 750VA XFMR single phase, 2A fuses on the primary side
- powers control circuit