Curious what would define as a series rated system and where others think a series rated system would start and end.
Example:
Available fault current at a fused service disconnect is 20,000.
The selected fuse limits the fault current on the load side to a value below 10,000 in the first half cycle.
The service disconnects supplys a feeder. The feeder has taps that supply multiple panelboards.
The panel board main breaker is rated for 10,000 as are the branch breakers.
I am aware of the what the code says in 240.86. This section uses the word circuit with no guidance on where the circuit begins. Also no guidance if upstream current limiting devices are considered when determining the available fault current at the line terminals of the downstream device.
Please let me know if you would consider this example a type of series rated system or not and why.
If it is not why would would it be important that a series rated label be required on a series system but nothing would be required for this example.
Thanks for your ideas and opions.
Example:
Available fault current at a fused service disconnect is 20,000.
The selected fuse limits the fault current on the load side to a value below 10,000 in the first half cycle.
The service disconnects supplys a feeder. The feeder has taps that supply multiple panelboards.
The panel board main breaker is rated for 10,000 as are the branch breakers.
I am aware of the what the code says in 240.86. This section uses the word circuit with no guidance on where the circuit begins. Also no guidance if upstream current limiting devices are considered when determining the available fault current at the line terminals of the downstream device.
Please let me know if you would consider this example a type of series rated system or not and why.
If it is not why would would it be important that a series rated label be required on a series system but nothing would be required for this example.
Thanks for your ideas and opions.