C CelectricB Member Location Texas Panhandle Occupation MEP Designer May 11, 2021 #1 I remember coming across a forum post that said the NEC allows conduit to be used for an EGC. Can anyone confirm where this is located?
I remember coming across a forum post that said the NEC allows conduit to be used for an EGC. Can anyone confirm where this is located?
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer May 11, 2021 #2 250.118. Note that some jurisdictions and some plan & spec projects specifically forbid this practice.
250.118. Note that some jurisdictions and some plan & spec projects specifically forbid this practice.
roger Moderator Staff member Location Fl Occupation Retired Electrician May 11, 2021 #3 However it is required in some areas, specifically 517.13 locations. Roger