Where is the article 430 reference on motors 6 Amps or greater?

gene6

Senior Member
Location
NY
Occupation
Electrician
I was told today that motors 6 amps or more need to be on individual circuits.
So say I have two 1/3 HP 120V pump motors and a GFCI to install do they each need a 20A circuit or can they share?
Each motor is about 7A nameplate.
Where is the article 430 reference on motors 6 Amps or more so I can read up on this?
 

gene6

Senior Member
Location
NY
Occupation
Electrician
Thank you sir.
So looking at 430.53 it seems I'll need 3 circuits one for each 1/3 HP pump and one for the GFCI receptacle.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
What about 430.53(B), if the motors have individual overload protection (are thermally protected)?

The Table 430.248 FLC for a 1/3 HP 115V motor is 7.2A. Per 430.52, 7.2A * 250% = 18A, and rounding up to a 20A OCPD is allowed. So each motor would properly protected for SCGF by a 20A branch circuit .

Cheers, Wayne
 

gene6

Senior Member
Location
NY
Occupation
Electrician
What about 430.53(B), if the motors have individual overload protection (are thermally protected)?

The Table 430.248 FLC for a 1/3 HP 115V motor is 7.2A. Per 430.52, 7.2A * 250% = 18A, and rounding up to a 20A OCPD is allowed. So each motor would properly protected for SCGF by a 20A branch circuit .

Cheers, Wayne
Yeah I could not tell if these sump pumps had individual overload protection though i imagine all small motors do? The foundation company we are working for was trying to be smart and quote code instead of just saying they just wanted 3 circuits or as Larry suggested a small sub-panel. I think its also for redundancy.
 