david
Senior Member
- Location
- Pennsylvania
NFPA 70-08 requires a service disconnect ( 230.90 Where Required.
Each ungrounded service conductor shall have overload protection. )
695.4(B)(1). Requires the overcurrent protection to be capable of caring lock rotor current.
I arrive on site there is an EATON 25 horse power 208 volt three phase fire pump controller being used as the service disconnect. The over current protection is being provided by an inverse time nonadjustable circuit breaker rated at 150 amps based on the provision found in NFPA 20 section 10.7.2.1 ( This equipment is listed as suitable for use as service equipment ) A rating falling between 150 and 250 percent of the motors full load amps.
Where do I find language in NFPA 70 that will accept this installation?
VII. Service Equipment ? Overcurrent Protection
230.90 Where Required.
Each ungrounded service conductor shall have overload protection.
Exception No. 4: Overload protection for fire pump supply conductors shall comply with 695.4(B)(1).
695.4 Continuity of Power. (B) Supervised Connection. A single disconnecting means and associated overcurrent protective device(s) shall be permitted to be installed between a remote power source and one of the following:
(1) Overcurrent Device Selection. The overcurrent protective device(s) shall be selected or set to carry indefinitely the sum of the locked-rotor current of the fire pump motor(s) and the pressure maintenance pump motor(s) and the full-load current of the associated fire pump accessory equipment when connected to this power supply.
Each ungrounded service conductor shall have overload protection. )
695.4(B)(1). Requires the overcurrent protection to be capable of caring lock rotor current.
I arrive on site there is an EATON 25 horse power 208 volt three phase fire pump controller being used as the service disconnect. The over current protection is being provided by an inverse time nonadjustable circuit breaker rated at 150 amps based on the provision found in NFPA 20 section 10.7.2.1 ( This equipment is listed as suitable for use as service equipment ) A rating falling between 150 and 250 percent of the motors full load amps.
Where do I find language in NFPA 70 that will accept this installation?
VII. Service Equipment ? Overcurrent Protection
230.90 Where Required.
Each ungrounded service conductor shall have overload protection.
Exception No. 4: Overload protection for fire pump supply conductors shall comply with 695.4(B)(1).
695.4 Continuity of Power. (B) Supervised Connection. A single disconnecting means and associated overcurrent protective device(s) shall be permitted to be installed between a remote power source and one of the following:
(1) Overcurrent Device Selection. The overcurrent protective device(s) shall be selected or set to carry indefinitely the sum of the locked-rotor current of the fire pump motor(s) and the pressure maintenance pump motor(s) and the full-load current of the associated fire pump accessory equipment when connected to this power supply.