According to Jim Dollard, NEC code-making panel member.
2020 NFPA-70, 310.14(A)(2) Where more than one ampacity applies..
Exception: ..the higher ampacity shall be permitted..
applies only to the impact of ambient temperature..
"..cannot be applied to correction factors on rooftops or for adjustment factors for more than three current-carrying conductors."
Source Q&A Article
This forum uses 210.14(A)(2) Exception on rooftops, regardless of CCC's that exceed table limits, contrary to Jim Dollard & inspector red tag.
If 310.14(A)(2) Exception excludes rooftops, and Adjustment factors that exceed table CCC's, where is that stated in the code language?